저압 옥내배전방식

제공

,
배전방식

배전설계 계획
저압옥내배선방식
직류송전방식과 교류송전방식의 비교

간선과 분기회로

목차(저압 옥내배전방식)
결선도공급전력 전선총량선전류 전선단면적전압강하배전손실
단상2선식\[P=EI_1\] \[V=2S_1L\]\[I_1\] \[100[\%]\]\[S_1\] \[100[\%]\]\[e_1=2I_1R_1\] \[=2\frac{I_1\rho L}{S_1}\] \[100[\%]\]\[Q_1=2I^2_1R_1\] \[=2I^2_1\frac{\rho L}{S_1}\] \[100\%\]
단상3선식\[P=2EI_2\] \[V=3S_2L\]\[I_2=\frac{I_1}{2}\] \[50[\%]\]\[S_2=\frac{2}{3} S_1\] \[66.7[\%]\]\[e_2=I_2R_2\] \[=(\frac{I_1}{2})\frac{\rho L}{S_2}\] \[=(\frac{I_1}{2})\frac{\rho L}{\frac{2}{3}S_1}\] \[=(\frac{3}{4})\frac{I_1 \rho L}{S_1}\] \[=\frac{3}{8}e_1\] \[37.5[\%]\]\[Q_2=2I^2_2R_2\] \[=2(\frac{I_1}{2})^2\frac{\rho L}{S_2}\] \[=(\frac{I_1^2}{2})\frac{\rho L}{\frac{2}{3}S_1}\] \[=(\frac{3}{4})\frac{I_1^2 \rho L}{S_1}\] \[=\frac{3}{8}Q_1\] \[37.5\%\]
3상3선식\[P=\sqrt3 EI_3\] \[V=3S_3L\]\[I_3=\frac{I_1}{\sqrt3}\] \[57.7[\%]\]\[S_3=\frac{2}{3}S_1\] \[66.7[\%]\]\[e_3=\sqrt 3I_3R_3\] \[=\sqrt3(\frac{I_1}{\sqrt3})\frac{\rho L}{S_3}\] \[=I_1\frac{\rho L}{\frac{2}{3}S_1}\] \[=(\frac{3}{2})\frac{I_1 \rho L}{S_1}\] \[=\frac{3}{4}e_1\] \[75[\%]\]\[Q_3=3I^2_3R_3\] \[=3(\frac{I_1}{\sqrt3})^2\frac{\rho L}{S_3}\] \[=I_1^2\frac{\rho L}{\frac{2}{3}S_1}\] \[=(\frac{3}{2})\frac{I_1^2 \rho L}{S_1}\] \[=\frac{3}{4}Q_1\] \[75\%\]
3상4선식\[P=3EI_4\] \[V=4S_4L\]\[I_4=\frac{I_1}{3}\] \[33.3[\%]\]\[S_4=\frac{1}{2}S_1\] \[50[\%]\]\[e_4=I_4R_4\] \[=(\frac{I_1}{3})\frac{\rho L}{S_4}\] \[=(\frac{I_1}{3})\frac{\rho L}{\frac{2}{1}S_1}\] \[=(\frac{3}{3})\frac{I_1 \rho L}{S_1}\] \[=\frac{1}{3}e_1\] \[33.3[\%]\]\[Q_4=3I^2_4R_4\] \[=3(\frac{I_1}{3})^2\frac{\rho L}{S_4}\] \[=(\frac{I_1^2}{3})\frac{\rho L}{\frac{1}{2}S_1}\] \[=(\frac{2}{3})\frac{I_1^2 \rho L}{S_1}\] \[=\frac{1}{3}Q_1\] \[33.3\%\]

1️⃣단상2선식
  • 결선도
  • 공급전력 전선총량
\[P=EI_1\] \[V=2S_1L\]
  • 선전류
\[I_1\] \[100[\%]\]
  • 전선단면적
\[S_1\] \[100[\%]\]
  • 전압강하
\[e_1=2I_1R_1\] \[=2\frac{I_1\rho L}{S_1}\] \[100[\%]\]
  • 배전손실
\[Q_1=2I^2_1R_1\] \[=2I^2_1\frac{\rho L}{S_1}\] \[100\%\]
2️⃣단상3선식
  • 결선도
  • 공급전력 전선총량
\[P=2EI_2\] \[V=3S_2L\]
  • 선전류
\[I_2=\frac{I_1}{2}\] \[50[\%]\]
  • 전선단면적
\[S_2=\frac{2}{3} S_1\] \[66.7[\%]\]
  • 전압강하
\[e_2=I_2R_2\] \[=(\frac{I_1}{2})\frac{\rho L}{S_2}\] \[=(\frac{I_1}{2})\frac{\rho L}{\frac{2}{3}S_1}\] \[=(\frac{3}{4})\frac{I_1 \rho L}{S_1}\] \[=\frac{3}{8}e_1\] \[37.5[\%]\]
  • 배전손실
\[Q_2=2I^2_2R_2\] \[=2(\frac{I_1}{2})^2\frac{\rho L}{S_2}\] \[=(\frac{I_1^2}{2})\frac{\rho L}{\frac{2}{3}S_1}\] \[=(\frac{3}{4})\frac{I_1^2 \rho L}{S_1}\] \[=\frac{3}{8}Q_1\] \[37.5\%\]
3️⃣3상3선식
  • 결선도
  • 공급전력 전선총량
\[P=\sqrt3 EI_3\] \[V=3S_3L\]
  • 선전류
\[I_3=\frac{I_1}{\sqrt3}\] \[57.7[\%]\]
  • 전선단면적
\[S_3=\frac{2}{3}S_1\] \[66.7[\%]\]
  • 전압강하
\[e_3=\sqrt 3I_3R_3\] \[=\sqrt3(\frac{I_1}{\sqrt3})\frac{\rho L}{S_3}\] \[=I_1\frac{\rho L}{\frac{2}{3}S_1}\] \[=(\frac{3}{2})\frac{I_1 \rho L}{S_1}\] \[=\frac{3}{4}e_1\] \[75[\%]\]
  • 배전손실
\[Q_3=3I^2_3R_3\] \[=3(\frac{I_1}{\sqrt3})^2\frac{\rho L}{S_3}\] \[=I_1^2\frac{\rho L}{\frac{2}{3}S_1}\] \[=(\frac{3}{2})\frac{I_1^2 \rho L}{S_1}\] \[=\frac{3}{4}Q_1\] \[75\%\]
4️⃣3상4선식
  • 결선도
  • 공급전력 전선총량
\[P=3EI_4\] \[V=4S_4L\]
  • 선전류
\[I_4=\frac{I_1}{3}\] \[33.3[\%]\]
  • 전선단면적
\[S_4=\frac{1}{2}S_1\] \[50[\%]\]
  • 전압강하
\[e_4=I_4R_4\] \[=(\frac{I_1}{3})\frac{\rho L}{S_4}\] \[=(\frac{I_1}{3})\frac{\rho L}{\frac{2}{1}S_1}\] \[=(\frac{3}{3})\frac{I_1 \rho L}{S_1}\] \[=\frac{1}{3}e_1\] \[33.3[\%]\]
  • 배전손실
\[Q_4=3I^2_4R_4\] \[=3(\frac{I_1}{3})^2\frac{\rho L}{S_4}\] \[=(\frac{I_1^2}{3})\frac{\rho L}{\frac{1}{2}S_1}\] \[=(\frac{2}{3})\frac{I_1^2 \rho L}{S_1}\] \[=\frac{1}{3}Q_1\] \[33.3\%\]

배전방식

배전설계 계획
저압옥내배선방식
직류송전방식과 교류송전방식의 비교

간선과 분기회로

목차(저압 옥내배전방식)

💯기출문제

●A1 저압옥내배전방식에 대하여 설명하시오 (133)

🌐V1015P24


코멘트

답글 남기기

이메일 주소는 공개되지 않습니다. 필수 필드는 *로 표시됩니다